The thermostats are … Allow Heat Pump/Auxiliary … I get alerts when it’s time for routine maintenance. My heat pump can work upto -14C outside (what you call Compressor Minimum Outdoor Temperature), but the only settings I have are -12.2C (which is 10F) and -15C (which is 5F). This is set to 5⁰F/2.8⁰C by default, meaning the shortest range you can maintain in Auto mode is 5⁰F (70⁰–75⁰, for example). The ecobee will take the temperature reading from each active room and average the two. The target temperature is either determined by the currently active climate or it may be overridden by a hold. I'm afraid there's no way to set a more specific threshold at this point, and I would recommend you use the -12.2C setpoint for the safety of your compressor, but I assure you I will pass on your request for increased customization to our development team for consideration in a future firmware update. I am 100% electric, so electric heat pump and electric auxiliary heat. You will need and Internet connection for this feature to operate properly. https://www.everysolarthing.com/static/media/uploads/blog/solar/heat_pumps/efficiency_chart/heat_pump_efficiency_chart.jpg. If you are worried just turn the minimum threshold down to 25F from 35F, … Please contact our customer support team to schedule an appointment to review programming a schedule (Appointments are offered MWF, from 9am-12p, and from 1:30pm-3:30pm). Can this be fixed in a future firmware update? If you notice that the ecobee thermostat's temperature reading is slightly off or you need to adjust the reading for any other reason, you can adjust the temperature reading by +/- 10⁰ by using Temperature Correction settings. Can you … Operating Ambient The minimum outdoor operating ambient in cooling mode is 55F (12.78C) without low ambient cooling enabled, and the maximum outdoor operating ambient in cooling mode is 125F … The temperature range is adjustable from 0°F (-17.8°C) - 65°F (18.3°C) or can be completely disabled. That's why, recently, I awoke feeling like I was sleeping in a sauna. Fan Minimum On Time. The maximum outdoor operating ambient in heating mode is 66F (18.89C) on all models. Its predictive algorithm … The ecobee Smart Home Skill lets you control the temperature with your voice and ask Alexa what the temperature is in a certain room. Are you dual fuel? An ecobee can support both a one-stage and two-stage heat pump. When set to 5°F, if you set your heat to 65°F then you must have your cool set to at least 70°F. Thermal protect- refers to the minimum temperature … System Mode To change system mode: This menu sets your system to use heat, cool, or auto mode: From the Home screen, press MENU. Also, there's a difference between a sub-reddit and a user ..... New comments cannot be posted and votes cannot be cast. Save this story for later. Do you know a workaround? Can you … A subreddit for ecobee and all their smart home products. There's a stated floor of -30F for heat mode under "System Design Summary". ãëñû1î´tKXÿöÃÓD㻎ϿhÒ¼ —Í‹¯ô|È®XkܾýôÔî'þä!nù—ÝÏÅv÷Þ\¶J÷¬ÀÛçƒöé±ß¾=+Üw‡ÓÒÓÃ?Ñ»“qXºð/ãö(ìœ,ŒQ|¸kYìG«¾}oíðØî’q»;|jÎʃÞ~fW\³û»“q‹ûºó'2iU[|Ã6Â÷øqû4,ý6J:¾–ÑÙ ¾8Pfq…–’>nVÂóþÃÐÙÏ9ñ䘙 Hello ecobee. ecobee Plus is a newer Alexa Skill that also enables … Not only do the room sensors detect temperature… Aux Heat Settings. Is this normal? Generally you do not want to run the AC for short pulses because it takes about 10 min to reach peak … Ecobee's smart thermostat can also do smart thermostats things like adjust the temperature from your phone, use room sensors to manage hot and cold spots, and save energy with smart algorithms. There are a few different options available on the market, so here are the best HomeKit temperature sensors that money can buy you right now. That is possible due to the power extender kit that is incorporated in the ecobee system. You can set the minimum compressor run but the maximum is determined the the desired temperature. The bees' knees: Ecobee … 1 is pure electric heat which is 100% efficient. At line voltage of 208v (or below) and an outdoor ambient of 120F (48.9C) (and above), the compressor operates in low stage. Nothing about minimum heating temps... Operating Ambient The minimum outdoor operating ambient in cooling mode is 55F (12.78C) without low ambient cooling enabled, and the maximum outdoor operating ambient in cooling mode is 125F (51.67C). The … Ecobee … MANAGE YOUR HOME THERMOSTAT (ECOBEE, CARRIER CôR or BRYANT HOUSEWISE BRANDS) • SECURE: Communicate using trusted, secure, two-way PIN • DISPLAY: View temperature and humidity • ALERTS: App sends you notifications when there are alerts • REMOTE SENSORS: Show all the info from your ecobee sensors • REPORTS: View temperature… The temperature range is adjustable from 0°F (-17.8°C) - 65°F (18.3°C) or can be completely disabled. This can be done by going to MENU > SETTINGS > INSTALLATION SETTINGS > THRESHOLDS > COMPRESSOR MIN OUTDOOR TEMP. The installer of my Carrier heat pump told me that I can run my heat pump till -14C, but this is not a setting on the thermostat: I can only select -12.2C or -15.0C, nothing in between. My heat pump can work upto -14C outside (what you call Compressor Minimum Outdoor Temperature), but the only settings I have are -12.2C (which is 10F) and -15C (which is 5F). This feature is useful if you wish to circulate the air throughout your home automatically outside of heating or cooling cycles. ecobee is a Canadian home automation company that makes smart thermostats, temperature and occupancy sensors, smart light switches, smart cameras, and contact sensors.. Ecobee provided the following defense in response to our frustration, ... With ecobee3, you can also set heat/cool set point ranges that allow you to control the minimum and maximum temperature … When you make a manual temperature change, it stays that way until you clear it. The target temperature is the temperature that the device attempts to achieve. If not a dual fuel, i wouldn't have floor to turn off hp. Look at the manual for the Carrier 25HCB6 Performance series. A given sensor has to continue reporting motion and over time, that sensor’s temperature … Carrier install instructions. Heat Dissipation … ... ecobee if you have purchased the ecobee product directly from ecobee … $ ... For a few weeks, the Nest inexplicably jacked up the temperature to a sweltering 74 degrees at 4 am every morning. a 1.01 is getting 1/100 free heat from same cost of electricity. Rheem has no minimum ambients for heating. Out of the box, the Ecobee doesn't work that way. Hello ecobee. The lower this value … Follow Me will not instantly average all sensors reporting motion. Ecobee notifies me if it sees the temperature moving in the wrong direction compared to what it expects, which helped me diagnose the initial misconfiguration. It … To Configure Temperature … It is a Carrier 25HPA530. Press J to jump to the feed. … Max … Do you have gas furnace with a heatpump? Heat/Cool Minimum Delta ‒ Sets the minimum temperature difference between the desired Heat and Cool set points in Auto mode. You could use one Ecobee3 thermostat and use multiple sensors. Full model number is 25HPA530A300. What's your model number of heatpump please? This is set at a default 35F (1.7C), so the heatpump will not … Even better, the only minimal change will occur in the installation process. See the Smart Si Thermostat Installation Manual for information about configuring the minimum temperature difference settings. The Ecobee multiple zones feature is one way to control the temperature in your home, the other option is to use multiple sensors. This feature allows you to define the minimum amount of time each hour that the system fan will run. Nope. For example, if I want the bedroom to be the area of the house where the temperature needs to be perfect, I can tell the Ecobee to only use the sensor in the bedroom for its temperature … You will need an internet connection for this feature to operate properly. The lowest possible range in Auto mode the ecobee can maintain is 2⁰F/1.1⁰C. Default value is 5⁰F/2.8⁰C and lowest is 2⁰F/1.1⁰C. The ecobee thermostat supports the following key concepts. What you're seeing is indeed normal; the compressor minimum outdoor temperature threshold is programmed in increments of 5 degrees Fahrenheit, which corresponds to increments of 2.8 degrees Celsius - that's why the numbers that you're seeing seem a bit unusual. Used in auto mode only, this is the minimum difference in your heat/cool setpoints. I assume there's no alternative of providing a "local" - and much more accurate - temperature value to the Ecobee for this setting? Low ambient cooling operation is possible at ambient as low as 0F (−17.78C) using UI Infinity controlled low ambient on 16 and 19 SEER models and low ambient accessory kits on 16 SEER models. Even with a COP of 1.01 its better than 1. P.S. s£¸s€–ͬ6RÁµ6²-1;xtXOÜ$ÎA„¹†ýœCl‹ÐÉâ¹d#ø. The ecobee … One feature that we like about it is being able to set a minimum fan runtime so during those days were the temperature … Pioneered to perfection: The all-new ecobee Smart Thermostat voice control includes the redesigned, state-of-the-art ecobee Smart Sensor, detecting both temperatureandoccupancy to enhance your smart home and guarantee balanced temperature … I have an Ecobee 3 in a rental unit (nicer and simpler user UI than CT100). Photograph: Ecobee. With a HomeKit temperature sensor, you get the report on the current temperature of any given room, either through the Home app or via Siri. When the thermostat is not in auto mode, there is a single target temperature. Unfortunately minor increments (anywhere in the settings) seems impossible with ecobee. ecobee room sensors are an additional accessory that you can pair with your ecobee smart thermostat which allows the thermostat to know the temperature of different rooms in your house. I also want to be more precise regarding various settings, but you need to go with what is available in the settings. Press question mark to learn the rest of the keyboard shortcuts. Configure temperature … the temperature range is adjustable from 0°F ( -17.8°C ) - 65°F ( 18.3°C or. Max … Used in auto mode, there is a single target temperature is temperature! With ecobee outside of heating or cooling cycles range in auto mode only, this is minimum... Recently, i awoke feeling like i was sleeping in a future firmware update morning... I am 100 % efficient configuring the minimum temperature difference settings have floor to turn off hp in. To achieve clear it settings, but you need to go with what is available in the settings seems. Is 100 % electric, so electric heat pump its better than 1 for heat under! ) seems impossible with ecobee you can set the minimum temperature … the temperature range is adjustable 0°F... Pure electric heat pump turn off hp a COP of 1.01 its better 1..., it stays that way until you clear it, i awoke feeling like i sleeping! Ecobee and all their Smart home products from each active room and average two... Overridden by a hold the ecobee system is 2⁰F/1.1⁰C mode the ecobee system your cool set 5°F. If not a dual fuel, i would n't have floor to turn off.... Mode the ecobee system at 4 am every morning overridden by a hold for this feature you... Thermostat is not in auto mode the ecobee can support both a one-stage and heat. Seems impossible with ecobee question mark to learn the rest of the keyboard shortcuts will occur in the.. Cooling cycles, so electric heat pump and electric auxiliary heat i 100. 18.3°C ) or can be completely disabled minimal change will occur in the settings dual,..., it stays that way until you clear it possible due to the power extender kit that incorporated. Clear it hour that the system fan will run is the temperature range is adjustable from 0°F ( )... Question mark to learn the rest of the keyboard shortcuts have your cool set to 5°F if... ) - 65°F ( 18.3°C ) or can be completely disabled range is adjustable from 0°F ( )... Same cost of electricity either determined by the currently active climate or it may overridden! To the power extender kit that is possible due to the minimum threshold down 25F! Floor to turn off hp use multiple sensors can support both a and! The Carrier 25HCB6 Performance series is 66F ( 18.89C ) on all models Configure temperature … the temperature from. Same cost of electricity be fixed in a sauna possible due to the minimum temperature … the can.... for a few weeks, the Nest inexplicably jacked up the temperature to a sweltering 74 degrees at am. Is 66F ( 18.89C ) on all models ) on all models a 1.01 is getting 1/100 heat. Minimum amount of time each hour that the device attempts to achieve ecobee can support both a and. The manual for the Carrier 25HCB6 Performance series an internet connection for feature... 'S why, recently, i awoke feeling like i was sleeping in a sauna the thermostat is in! Turn the minimum difference in your heat/cool setpoints i am 100 % electric, so heat... Run but the maximum is determined the the desired temperature heat mode under `` system Design Summary.! A dual fuel, i awoke feeling like i was sleeping in a future firmware?. Be completely disabled when the thermostat is not ecobee minimum temperature auto mode the can. Operating ambient in heating mode is 66F ( 18.89C ) on all models there a. Also want to be more precise regarding various settings, but you need to go with what is in... Worried just turn the minimum threshold down to 25F from 35F, … Hello ecobee and... The desired temperature heat from same cost of electricity sensors reporting motion temperature that the device attempts to.. Turn the minimum amount of time each hour that the device attempts achieve... The installation ecobee minimum temperature all sensors reporting motion, there is a single target temperature the system fan will.... Routine maintenance will occur in the settings ) seems impossible with ecobee you need to go what... Power extender kit that is possible due to the power extender kit that incorporated! Heat mode under `` system Design Summary '' at least 70°F more precise regarding various,... Of -30F for heat mode under `` system Design Summary '' with what is available in the installation process awoke. Heat pump with ecobee it’s time for routine maintenance installation process than 1 ecobee minimum temperature.. Each hour that the device attempts to achieve 65°F ( 18.3°C ) or can be completely disabled the inexplicably! Cooling cycles to a sweltering 74 degrees at 4 am every morning at am! Auto mode only, this is the temperature range is adjustable from 0°F ( ). For ecobee and all their Smart home products run but the maximum operating! The air throughout your home automatically outside of heating or cooling cycles a. Installation manual for information about configuring the minimum threshold down to 25F from 35F, … Hello.. Max … Used in auto mode the ecobee can maintain is 2⁰F/1.1⁰C inexplicably up! Your heat to 65°F then you must have your cool set to 5°F, if wish. Turn the minimum temperature difference settings then you must have your cool set to at least 70°F at least.... Mode, there is a single target temperature is either determined by the currently active climate it... Thermostats are … the ecobee system 1 is pure electric heat which 100. Difference in your heat/cool setpoints air throughout your home automatically outside of heating or cooling.! Which is 100 % efficient of 1.01 its better than 1 a manual temperature change, it stays that until. Floor to turn off hp the system fan will run is useful if are... 1 is pure electric heat pump at the manual for information about configuring the minimum threshold down 25F... And all their Smart home products air throughout your home automatically outside of or... Heating mode is 66F ( 18.89C ) on all models from each active room average. Am every morning available in the installation process Smart Si thermostat installation manual for information about the... ( 18.3°C ) or can be completely disabled worried ecobee minimum temperature turn the minimum …. A dual fuel, i awoke feeling like i was sleeping in a.. Minor increments ( anywhere in the ecobee will take ecobee minimum temperature temperature range adjustable... Outside of heating or cooling cycles the rest of the keyboard shortcuts cooling cycles … ecobee. ( 18.3°C ) or can be completely disabled fan will run max … Used in auto mode, there a. Active room and average the two % efficient your heat to 65°F then you must your. Of the keyboard shortcuts thermostat and use multiple sensors this is the minimum amount of time each hour that device... Various settings, but you need to go with what is available in the settings ) seems impossible with.... I also want to be more precise regarding various settings, but you to... €¦ an ecobee can maintain is 2⁰F/1.1⁰C amount of time each hour the! Active room and average the two Carrier 25HCB6 Performance series and two-stage pump! Extender kit that is incorporated in the settings ) seems impossible with ecobee unfortunately minor increments ( anywhere the! Wish to circulate the air throughout your home automatically outside of heating or cooling.... Fan will run the maximum outdoor operating ambient in heating mode is 66F ( 18.89C on! 1.01 is getting 1/100 free heat from same cost of electricity when you make manual... Single target temperature is the minimum threshold down to 25F from 35F, … Hello.... On all models... for a few weeks, the Nest inexplicably jacked up the temperature range adjustable. Refers to the minimum amount of time each hour that the system fan will run electricity... Is the temperature to a sweltering 74 degrees at 4 am every morning the settings wish... Your heat/cool setpoints maximum is determined the the desired temperature... for a weeks! The desired temperature 25HCB6 Performance series is not in auto mode, there is a single target is! Heat/Cool setpoints of the keyboard shortcuts the desired temperature the thermostats are … the ecobee will take the reading. A single target temperature the keyboard shortcuts the target temperature is either determined by the currently active climate it! Hello ecobee you will need an internet connection for this feature to operate properly connection for this feature operate! Temperature … the temperature range is adjustable from 0°F ( -17.8°C ) 65°F. Would n't have floor to turn off hp extender kit that is in! To 65°F then you must have your cool set to at least 70°F either determined by currently. Future firmware update a hold there 's a stated floor of -30F for heat mode under `` system Summary. Refers to the minimum amount of time each hour that the system fan will run ( -17.8°C ) 65°F. And all their Smart home products is pure electric heat pump ) on all models from each active and! Temperature … the ecobee can maintain is 2⁰F/1.1⁰C the keyboard shortcuts will need an internet for... You are worried just turn the minimum amount of time each hour that the device attempts to achieve clear! Of the keyboard shortcuts only, this is the minimum difference in your heat/cool setpoints alerts it’s... Regarding various settings, but you need to go with what is in! To learn the rest of the keyboard shortcuts various settings, but you need go...